Question 13050 of 844 · Washington 01 Journey Level Electrician Exam

What is the ampacity of 4 AWG THWN copper (75 °C insulation) with three current-carrying conductors at an ambient of 45 °C?

Exactly one answer is correct.

Show solution

Correct answer to question 13050

  • B: 69.7 A

Explanation

THWN is a 75 °C insulation, so the base ampacity is 85 A and the 75 °C correction factor for 41 to 45 °C is 0.82: 85 x 0.82 = 69.7 A. Using the 90 °C factor 0.87 gives 74.0 A, which does not apply to THWN.