Question 13048 of 844 · Washington 01 Journey Level Electrician Exam

Nine current-carrying 12 AWG THHN copper conductors are installed in one conduit at 30 °C ambient. What is the adjusted ampacity of each conductor based on the 90 °C column?

Exactly one answer is correct.

Show solution

Correct answer to question 13048

  • D: 21 A

Explanation

12 AWG copper has a 90 °C ampacity of 30 A, and 7 to 9 current-carrying conductors take a 70 % adjustment: 30 x 0.70 = 21 A. 24 A uses the 80 % factor for 4 to 6 conductors.

Next to question ›