Question 13118 of 844 · Washington 01 Journey Level Electrician Exam
A single-phase 240 volt, 10 kW heater operates for 3 hours. How many kilowatt-hours does it use, and what is its current?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13118
- B: 30 kWh, 41.7 A
Explanation
Energy is 10 kW x 3 h = 30 kWh, and current is 10,000 / 240 = 41.7 A. 83.3 A results from dividing by 120 V, and 24.1 A from dividing by 1.732 as well.
More questions: Electrical Calculations
- 13119What is the circular mil area of a 10 AWG conductor as listed in Chapter 9 Table 8?
- 13120A 240 volt, single-phase, 2 hp motor has a table full-load current of 12 A at 230 volts. What is the minimum branch-circuit conductor ampacity?
- 13121Three-phase 460 volt motors are rated 5 hp (7.6 A) and 3 hp (4.8 A). What is the minimum ampacity of a feeder supplying only these two motors?
- 13122A 9 kW, 480 volt, three-phase resistive heater is a continuous load. What is the minimum standard overcurrent device rating?
- 13123What is the inverse time breaker maximum for a 3 hp, 230 volt, single-phase motor (table FLC 17 A), allowing the next higher standard size?
- 13001A resistive heating element has a resistance of 15 ohms and is connected to 120 volts. What current does it draw?