A 240 volt, single-phase, 2 hp motor has a table full-load current of 12 A at 230 volts. What is the minimum branch-circuit conductor ampacity?

Exactly one answer is correct.

Show solution

Correct answer to question 13120

  • D: 15 A

Explanation

Motor branch-circuit conductors need 125 % of the table current: 12 x 1.25 = 15 A. 30 A would be 125 % of the 115 V current of 24 A.