WAC 296-46B adds a Washington requirement that a new building on a permanent concrete foundation must use which grounding electrode?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 14089
- A: A concrete encased electrode
Explanation
WAC 296-46B-250 requires a concrete encased grounding electrode at each new building or structure on a permanent concrete foundation, except mobile or manufactured homes. The electrode must comply with NEC 250.52(A)(3).