Question 2057 of 844 · Washington 01 Journey Level Electrician Exam
What is the maximum number of disconnects permitted for a building supplied by one outside feeder?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2057
- B: Six
Explanation
A building supplied by a feeder may have one disconnect or up to six grouped disconnects. This parallels the service rule. See 225.33.
More questions: Services and Service Equipment
- 2058What is the minimum height above finished grade for the point of attachment of a service drop to a building?
- 2059Ground-fault protection of equipment is required for a service disconnect rated 1200 A on which system?
- 2061Overhead feeder conductors run from a house to a detached garage at 120/240 volts. What is the minimum clearance above the residential driveway?
- 2062May branch circuit conductors be installed in the same raceway as service-entrance conductors?
- 2002What is the maximum number of service disconnects permitted for one service?
- 2004A 120/240 volt service drop passes over a roof with a slope of 4 in 12. What is the minimum clearance above the roof permitted by the exception for sloped roofs?