How long must a load run to be considered a continuous load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3013
- D: 3 hours or more
Explanation
A continuous load is one where the maximum current is expected to continue for 3 hours or more. See the definition in Article 100.