Question 3014 of 844 · Washington 01 Journey Level Electrician Exam
Which of the following is not a standard ampere rating for an inverse time circuit breaker?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3014
- B: 275 A
Explanation
Standard ratings in this range are 200, 225, 250, 300 and 350 A. There is no standard 275 A rating. See 240.6(A).
More questions: Feeders and Overcurrent Protection
- 3015Under the 25 ft feeder tap rule, what minimum ampacity must the tap conductors have?
- 3016In a dwelling unit, in which location are OCPDs prohibited?
- 3017Which situation is an exception to the small conductor rule?
- 3018Transformer secondary conductors not over 25 ft long must have an ampacity of at least what value?
- 3019What must the interrupting rating of a circuit breaker be at least equal to?
- 3020Why may an OCPD panelboard not be installed in a clothes closet?