Under the high-bay manufacturing tap rule, what is the maximum total length of the feeder tap?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3049
- B: 100 ft
Explanation
In high-bay manufacturing buildings over 35 ft high at the walls, with qualified maintenance, taps may be up to 100 ft in total with not more than 25 ft horizontal. The tap ampacity must be at least one-third of the feeder OCPD rating. See 240.21(B)(4).
More questions: Feeders and Overcurrent Protection
- 3050Which of the following is a standard ampere rating for fuses and inverse time circuit breakers?
- 3051A circuit breaker used to switch 120 volt fluorescent lighting on a regular basis must be marked with which designation?
- 3052The informational note for feeder conductor sizing recommends that feeder voltage drop not exceed what percentage?
- 3001Which location is prohibited for an OCPD in all three editions?
- 3002When the handle of a circuit breaker is operated vertically, what position must be the on position?
- 3004A series combination rating may not be used when motors connected between the two devices contribute more than what percentage of the lower-rated breaker's interrupting rating?