Question 4004 of 1033 · Washington 01 Journey Level Electrician Exam
A 240-volt, 30-ampere receptacle for an electric clothes dryer is installed in the laundry area of a single-family dwelling. Does it require GFCI protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4004
- A: Yes, laundry area receptacles from 125 through 250 volts are covered
Explanation
The dwelling GFCI rule in 210.8(A) covers 125-volt through 250-volt receptacles on single-phase circuits rated 150 volts or less to ground, and laundry areas are a listed location. A 240-volt dryer receptacle in the laundry area therefore needs GFCI protection.
More questions: Branch Circuits, GFCI and AFCI
- 4005Under the 2020 NEC, a 125-volt, 15-ampere receptacle installed behind the refrigerator in a dwelling kitchen does not serve the countertop and is more than 6 ft from the sink. Is GFCI protection required?
- 4008Under the 2020 NEC, a dwelling family room has a wet bar with a sink but no cooking provisions. A receptacle in the bar area is 8 ft from the sink. Is GFCI protection required by 210.8(A)?
- 4009A dwelling has a fully finished basement used as a recreation room. Do the 125-volt receptacles in this finished basement require GFCI protection?
- 4010A single 125-volt receptacle in an attached dwelling garage is dedicated to a chest freezer. Is GFCI protection required?
- 4012Under the 2020 NEC, a detached dwelling storage shed has a wood floor framed 2 ft above grade and is not habitable. Do the 125-volt receptacles inside require GFCI protection under 210.8(A)?
- 4013Where must a GFCI device that provides the protection required by 210.8 be located?