Question 4005 of 844 · Washington 01 Journey Level Electrician Exam
Under the 2020 NEC, a 125-volt, 15-ampere receptacle installed behind the refrigerator in a dwelling kitchen does not serve the countertop and is more than 6 ft from the sink. Is GFCI protection required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4005
- B: No, only kitchen receptacles serving countertop surfaces are covered
Explanation
In the 2020 NEC, 210.8(A) limited the kitchen item to receptacles installed to serve the countertop surfaces. A refrigerator receptacle that does not serve the countertop and is more than 6 ft from a sink was not covered by this rule.