Where must a GFCI device that provides the protection required by 210.8 be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4013
- B: In a readily accessible location
Explanation
210.8 requires the ground-fault circuit-interrupter to be installed in a readily accessible location. A GFCI receptacle hidden behind an appliance would not meet this rule, but a GFCI breaker or an accessible upstream device would.