When applying the 6 ft sink and bathtub distances in 210.8, how is the distance to a receptacle measured?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4014
- D: The shortest path a cord would follow without passing through a wall or door
Explanation
210.8 says the distance is the shortest path the cord of an appliance would follow without piercing a floor, wall, ceiling or fixed barrier, or passing through a door, doorway or window. A receptacle on the other side of a wall may therefore be farther away than it looks.