Question 4020 of 1033 · Washington 01 Journey Level Electrician Exam
For other than dwelling units, what is the maximum rating of a single-phase receptacle covered by the GFCI requirements of 210.8(B), on circuits rated 150 volts or less to ground?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4020
- B: 50 amperes
Explanation
210.8(B) covers single-phase receptacles rated 150 volts or less to ground and 50 amperes or less in the listed locations. Three-phase receptacles have a separate limit of 100 amperes.
More questions: Branch Circuits, GFCI and AFCI
- 4021For other than dwelling units, what is the maximum rating of a three-phase receptacle covered by the GFCI requirements of 210.8(B), on systems of 150 volts or less to ground?
- 4022In a commercial building, which of the following areas is excluded from the garage and service bay GFCI requirement in 210.8(B)?
- 4023A receptacle in a commercial building is located in an unfinished basement area used for storage. Is GFCI protection required?
- 4024A 125-volt receptacle in an office break room is 4 ft from the break room sink. Is GFCI protection required?
- 4025In a dwelling unit, what does the NEC require for the outlet that supplies a dishwasher?
- 4026Under the 2020 NEC, a 50-ampere range receptacle in a dwelling kitchen is located more than 6 ft from the sink and does not serve the countertop. Is GFCI protection required?