A metal underground water pipe qualifies as a grounding electrode only if it is in direct contact with the earth for at least what length?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5002
- B: 10 ft
Explanation
A metal underground water pipe must be in direct earth contact for 10 ft or more, including any metal well casing bonded to it, to qualify as an electrode. See 250.52(A)(1).