Question 5007 of 844 · Washington 01 Journey Level Electrician Exam
A ground ring encircling a building must consist of at least 20 ft of bare copper conductor not smaller than
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5007
- C: 2 AWG
Explanation
A ground ring must be in direct contact with the earth, encircle the building, and consist of at least 20 ft of bare copper not smaller than 2 AWG. See 250.52(A)(4).
More questions: Grounding and Bonding
- 5008What is the minimum length of a rod or pipe grounding electrode?
- 5010Where rock bottom prevents driving a ground rod vertically, the rod may be driven at an angle not exceeding what from vertical?
- 5011A single rod electrode does not need a supplemental electrode only if its resistance to earth is
- 5012Where two ground rods are installed to meet the supplemental electrode requirement, they must be spaced at least how far apart?
- 5013A ground rod measured 40 ohms, so a second rod was driven 6 ft away. The pair still measures 30 ohms. What else is required?
- 5014Which of the following is NOT permitted to be used as a grounding electrode?