Question 5008 of 844 · Washington 01 Journey Level Electrician Exam
What is the minimum length of a rod or pipe grounding electrode?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5008
- D: 8 ft
Explanation
Rod and pipe electrodes must be at least 8 ft long, and at least 8 ft of length must be in contact with the soil. See 250.52(A)(5) and 250.53.
More questions: Grounding and Bonding
- 5010Where rock bottom prevents driving a ground rod vertically, the rod may be driven at an angle not exceeding what from vertical?
- 5011A single rod electrode does not need a supplemental electrode only if its resistance to earth is
- 5012Where two ground rods are installed to meet the supplemental electrode requirement, they must be spaced at least how far apart?
- 5013A ground rod measured 40 ohms, so a second rod was driven 6 ft away. The pair still measures 30 ohms. What else is required?
- 5014Which of the following is NOT permitted to be used as a grounding electrode?
- 5015The portion of a grounding electrode conductor that is the sole connection to one or more ground rods is not required to be larger than