Question 5023 of 844 · Washington 01 Journey Level Electrician Exam
How must an 8 AWG copper grounding electrode conductor be installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5023
- C: Protected in a raceway or cable armor
Explanation
GECs smaller than 6 AWG must be protected in RMC, IMC, PVC, RTRC, EMT, or cable armor. See 250.64(B).