A service has four parallel sets of 500 kcmil copper per phase (2000 kcmil total). What is the minimum copper main bonding jumper?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5032
- D: 250 kcmil
Explanation
Above 1100 kcmil copper, the main bonding jumper must have an area of at least 12.5 percent of the largest ungrounded conductor set. 2000 x 0.125 = 250 kcmil. See 250.28(D) and Table 250.102(C)(1).
More questions: Grounding and Bonding
- 5033A subpanel in the same building is fed by a feeder from the service. How must the grounded (neutral) conductor be treated at the subpanel?
- 5034For a grounded service, the GEC connection to the grounded service conductor is permitted
- 5035What is the minimum copper equipment grounding conductor for a circuit protected by a 20 A OCPD?
- 5036What is the minimum copper equipment grounding conductor for a feeder protected by a 100 A OCPD?
- 5037What is the minimum copper equipment grounding conductor for a feeder protected by a 400 A OCPD?
- 5038A 20 A branch circuit is upsized from 12 AWG to 10 AWG copper to limit voltage drop. What is the minimum copper EGC?