Question 5033 of 844 · Washington 01 Journey Level Electrician Exam

A subpanel in the same building is fed by a feeder from the service. How must the grounded (neutral) conductor be treated at the subpanel?

Exactly one answer is correct.

Show solution

Correct answer to question 5033

  • A: Isolated from the enclosure and the EGC bar

Explanation

A grounded conductor may not be connected to normally non-current-carrying metal parts or EGCs on the load side of the service disconnect. Bonding there would put neutral current on the EGCs. See 250.24(A)(5) and 250.142(B).