Question 5027 of 844 · Washington 01 Journey Level Electrician Exam
A ferrous metal raceway that encloses a grounding electrode conductor must be
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5027
- C: Bonded at each end of the raceway
Explanation
Ferrous enclosures around a GEC act as a choke unless bonded, so they must be electrically continuous and bonded at both ends to the GEC or enclosure. See 250.64(E).
More questions: Grounding and Bonding
- 5030At the service, the main bonding jumper connects
- 5031What is the minimum size copper main bonding jumper for a service with 4/0 AWG copper ungrounded conductors?
- 5032A service has four parallel sets of 500 kcmil copper per phase (2000 kcmil total). What is the minimum copper main bonding jumper?
- 5033A subpanel in the same building is fed by a feeder from the service. How must the grounded (neutral) conductor be treated at the subpanel?
- 5034For a grounded service, the GEC connection to the grounded service conductor is permitted
- 5035What is the minimum copper equipment grounding conductor for a circuit protected by a 20 A OCPD?