A transformer supplies 250 kcmil copper secondary conductors. What is the minimum copper GEC for this separately derived system?

Exactly one answer is correct.

Show solution

Correct answer to question 5055

  • C: 2 AWG

Explanation

The GEC for a separately derived system is sized from Table 250.66 based on the derived ungrounded conductors. 250 kcmil copper is over 3/0 through 350 kcmil, so 2 AWG copper is required. See 250.30(A)(5).