Question 5059 of 844 · Washington 01 Journey Level Electrician Exam
Which of these AC systems is required to be grounded?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5059
- C: 120/240 V, single-phase, 3-wire
Explanation
Systems where the maximum voltage to ground on the ungrounded conductors does not exceed 150 V, such as 120/240 V single-phase, must be grounded. The other systems are permitted or required to be ungrounded. See 250.20.