Which of the following shall NOT be used to connect EGCs or bonding jumpers to enclosures?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5061
- A: Sheet metal screws
Explanation
Sheet metal screws are prohibited for connecting grounding and bonding conductors to enclosures. The other methods are recognized connection means. See 250.8.