An equipment bonding jumper on the load side of an OCPD is sized according to
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5062
- B: Table 250.122 based on the largest OCPD supplying the circuits
Explanation
Load-side equipment bonding jumpers are sized from Table 250.122 based on the rating of the largest OCPD supplying circuits within the raceway or enclosure. See 250.102(D).
More questions: Grounding and Bonding