A cable run parallel to a wood framing member must be kept at least how far from the nearest edge of the member where nails or screws are likely to penetrate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6014
- B: 1 1/4 in
Explanation
Cables and raceways installed parallel to framing members or furring strips must be at least 1 1/4 in from the nearest edge or be protected by a steel plate. See 300.4 in NEC 2020 and 2023 (300.6 in NEC 2026).