Under NEC 2020 and 2023, a cable run under metal-corrugated sheet roof decking must be kept at least how far from the lowest surface of the decking?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6015
- C: 1 1/2 in
Explanation
Cables and raceways under metal-corrugated sheet roof decking must be at least 1 1/2 in from the lowest surface of the decking to protect them from roofing screws. See 300.4(E).