Question 6029 of 1033 · Washington 01 Journey Level Electrician Exam
In an accessible suspended ceiling, an unsupported length of MC cable from the last support to a luminaire is permitted up to
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6029
- A: 6 ft
Explanation
MC cable may be unsupported for lengths up to 6 ft from the last point of support to the equipment or luminaire within an accessible ceiling. See 330.30(D).