Question 6031 of 966 · Washington 01 Journey Level Electrician Exam
May a raceway be used as the means of support for other cables, such as thermostat wiring, under the general rule?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6031
- C: No, unless identified for the purpose or as specifically permitted
Explanation
Raceways may not be used as a means of support for other raceways, cables, or nonelectrical equipment unless the raceway is identified for that purpose or another exception applies, such as Class 2 control wiring for the equipment served by the raceway. See 300.11 in NEC 2020 and 2023 (300.13 in NEC 2026).
More questions: Wiring Methods, Conductors and Boxes
- 6033In NEC 2020 and 2023, what is the maximum total of bends permitted in a run of EMT between pull points?
- 6035A conduit run between two boxes has two 90 degree bends and four 30 degree offset bends. How many more degrees of bend may be added before a pull point is required?
- 6036After cutting EMT, what must be done to the cut ends?
- 6037What is the maximum percent fill of a conduit containing three or more conductors?
- 6038A conduit nipple not exceeding 24 in long between boxes may be filled to what percent of its area?
- 6039When calculating conduit fill, how are equipment grounding conductors treated?