A conduit nipple not exceeding 24 in long between boxes may be filled to what percent of its area?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6038
- B: 60 percent
Explanation
Nipples 24 in or shorter may be filled to 60 percent of their total cross-sectional area, and the adjustment factors for more than three current-carrying conductors do not apply to them. See Chapter 9 notes to tables.
More questions: Wiring Methods, Conductors and Boxes
- 6039When calculating conduit fill, how are equipment grounding conductors treated?
- 6040What volume allowance does the box fill table assign to each 12 AWG conductor?
- 6041In a box fill calculation, a single receptacle on one yoke counts as
- 6042Two equipment grounding conductors enter a box. How are they counted for box fill?
- 6043A box contains four 12 AWG circuit conductors, two 12 AWG EGCs, and one switch on a single yoke. No clamps or fittings. What is the minimum box volume?
- 6044Outlet boxes for ceiling-suspended paddle fans must be listed and marked for fan support. What is the maximum fan weight such a box may support?