Question 6035 of 844 · Washington 01 Journey Level Electrician Exam
A conduit run between two boxes has two 90 degree bends and four 30 degree offset bends. How many more degrees of bend may be added before a pull point is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6035
- C: 60 degrees
Explanation
The run already has 2 x 90 + 4 x 30 = 300 degrees. The limit between pull points is 360 degrees, so only 60 degrees more may be added. See the bend rules in the raceway articles (300.24 in NEC 2026).
More questions: Wiring Methods, Conductors and Boxes
- 6036After cutting EMT, what must be done to the cut ends?
- 6037What is the maximum percent fill of a conduit containing three or more conductors?
- 6038A conduit nipple not exceeding 24 in long between boxes may be filled to what percent of its area?
- 6039When calculating conduit fill, how are equipment grounding conductors treated?
- 6040What volume allowance does the box fill table assign to each 12 AWG conductor?
- 6041In a box fill calculation, a single receptacle on one yoke counts as