Question 6061 of 966 · Washington 01 Journey Level Electrician Exam
Conductors of a circuit rated 600 V and a circuit rated 120 V may occupy the same raceway only if
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6061
- A: All conductors have insulation rated for the highest voltage present
Explanation
Conductors of circuits with different voltages may share a raceway, cable, or enclosure only if every conductor has insulation rated at least for the highest voltage present. That rule is 300.3(C)(1) in NEC 2020 and 2023 and 300.5(C)(1) in NEC 2026. Here the 600 V circuit sets the required insulation rating for the 120 V conductors too.
More questions: Wiring Methods, Conductors and Boxes
- 6062Why must all conductors of a circuit, including the neutral and EGC, be in the same metal raceway?
- 6063Which use of a flexible cord is prohibited?
- 6066Which location permits Type NM cable?
- 6067In an attic reached only by a scuttle hole, NM cable run across the top of joists must be protected by guard strips within what distance of the scuttle hole?
- 6068In an unfinished basement, NM cable run at angles to joists must be run through bored holes or on running boards if it is smaller than
- 6069The ampacity of NM cable conductors is generally determined using which temperature column?