Question 7004 of 966 · Washington 01 Journey Level Electrician Exam
A 15 ampere, 125 volt nonlocking receptacle is installed on an exterior wall of a house where it will be exposed to rain. Besides a suitable cover, what type of receptacle is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7004
- A: A listed weather-resistant type
Explanation
Section 406.9 requires 15 and 20 ampere, 125 and 250 volt nonlocking receptacles in damp and wet locations to be listed weather-resistant types. These devices use materials that resist UV exposure and corrosion. At a dwelling the receptacle must also be tamper resistant, but that alone does not satisfy 406.9.
More questions: Equipment, Devices and Luminaires
- 7005A 20 ampere, 125 volt receptacle is installed in a wet location. What kind of enclosure or cover is required?
- 7006A receptacle is installed under a roofed open porch where it is protected from beating rain (a damp location). What cover is the minimum requirement?
- 7007An electrician replaces a receptacle in a box that contains an equipment grounding conductor. What must the replacement be?
- 7008A two-wire receptacle circuit has no equipment grounding conductor. Which replacement is permitted without adding a grounding conductor?
- 7009Grounding-type receptacles are installed downstream of a GFCI on a circuit that has no equipment grounding conductor. How must they be marked?
- 7010An old receptacle in a location where the current code requires GFCI protection is being replaced. What does the code require?