Question 7005 of 1033 · Washington 01 Journey Level Electrician Exam
A 20 ampere, 125 volt receptacle is installed in a wet location. What kind of enclosure or cover is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7005
- C: One that stays weatherproof whether or not a plug is inserted (in-use type)
Explanation
Section 406.9(B)(1) requires an in-use type enclosure for 15 and 20 ampere receptacles in wet locations, so the receptacle stays protected while a cord is plugged in. The extra-duty listing applies only to outlet box hoods, not to every in-use product. A cover that seals only when closed and unplugged is not enough.
More questions: Equipment, Devices and Luminaires
- 7006A receptacle is installed under a roofed open porch where it is protected from beating rain (a damp location). What cover is the minimum requirement?
- 7007An electrician replaces a receptacle in a box that contains an equipment grounding conductor. What must the replacement be?
- 7008A two-wire receptacle circuit has no equipment grounding conductor. Which replacement is permitted without adding a grounding conductor?
- 7009Grounding-type receptacles are installed downstream of a GFCI on a circuit that has no equipment grounding conductor. How must they be marked?
- 7010An old receptacle in a location where the current code requires GFCI protection is being replaced. What does the code require?
- 7011A receptacle is replaced in a dwelling bedroom where the current code requires tamper-resistant receptacles. What must be installed?