A motor disconnect switch for a 10 hp motor must be rated in which unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8023
- D: Horsepower
Explanation
Section 430.109(A)(1) generally requires a motor-circuit switch to be rated in horsepower. Molded case breakers and switches and other listed devices are also permitted.