Question 8022 of 844 · Washington 01 Journey Level Electrician Exam
What is the minimum ampere rating of a motor disconnecting means for a motor rated 1000 volts or less?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8022
- D: 115 percent of the motor full-load current
Explanation
Section 430.110(A) requires the disconnecting means for motor circuits rated 1000 volts or less to have an ampere rating of at least 115 percent of the full-load current rating of the motor.