Question 8021 of 844 · Washington 01 Journey Level Electrician Exam
What does the NEC mean when it says equipment is in sight from other equipment?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8021
- B: Visible and not more than 50 ft away
Explanation
Article 100 defines in sight from as visible and not more than 50 ft distant from the other equipment. Both conditions must be met.
More questions: Motors, HVAC, Generators and Transformers
- 8022What is the minimum ampere rating of a motor disconnecting means for a motor rated 1000 volts or less?
- 8023A motor disconnect switch for a 10 hp motor must be rated in which unit?
- 8024How many conductors must a motor disconnecting means open?
- 8025What must a motor disconnecting means clearly indicate?
- 8027What is the minimum rating of a motor controller?
- 8028Where must the disconnecting means for a motor control circuit be arranged?