Question 8048 of 844 · Washington 01 Journey Level Electrician Exam
A single-phase cord-and-plug connected room air conditioner needs what protection device in or on the cord?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8048
- C: A leakage-current detector-interrupter (LCDI) or an AFCI
Explanation
Section 440.65 requires single-phase cord-and-plug connected room air conditioners to have a factory-installed LCDI or AFCI. It detects cord damage and opens the circuit before a fire starts.