Correct answer to question 8055
- C: 125 volt, 15 and 20 ampere receptacles
Explanation
Section 445.20 requires listed GFCI protection for the 125 volt, 15 and 20 ampere receptacle outlets on portable generators rated 15 kW or smaller. The protection can be integral to the generator or to the receptacles. The same section applies to bonded and unbonded generators.
More questions: Motors, HVAC, Generators and Transformers
- 8056A permanently installed optional standby generator supplies a home. What must prevent it from feeding back into the utility system?
- 8057Within how many seconds must an emergency system provide power after loss of normal supply?
- 8058Within how many seconds must a legally required standby system provide power after loss of normal supply?
- 8059An optional standby system uses an automatic transfer switch and no load management. What capacity must the system have?
- 8060Under the 2020 and 2023 NEC, a permanently installed generator at a one- or two-family dwelling needs which additional device?
- 8061A transformer rated 1000 volts or less has primary protection only, and the primary current is 9 A or more. What is the maximum primary overcurrent device rating?