A 45 kVA, 480 volt three-phase transformer has primary-only protection. What is the maximum standard primary breaker size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8066
- C: 70 A
Explanation
Primary current is 45,000 VA divided by (480 V times 1.732), which is about 54.1 A. Table 450.3(B) allows 125 percent, or 67.7 A, and its note permits the next higher standard size of 70 A.