Question 10019 of 966 · Washington 01 Journey Level Electrician Exam
What is the minimum clearance over a pool water surface for an insulated overhead service drop of 0 to 750 volts supported on a messenger with a grounded neutral?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10019
- B: 22.5 ft
Explanation
The table of overhead conductor clearances over pools gives 22.5 ft above the water surface or base of the diving platform for insulated cables of 0 to 750 volts supported on a solidly grounded bare messenger or neutral. Other conductor types, such as bare open conductors, need greater clearance.
More questions: Special Equipment, Pools, PV and EV
- 10020Unless listed for a lesser depth, the top of the lens of a wet-niche luminaire must be at least how far below the normal water level?
- 10021A branch circuit supplies an underwater pool luminaire operating above the low-voltage contact limit. What protection is required?
- 10022For sinusoidal ac, the low-voltage contact limit used in Article 680 is how many volts RMS?
- 10025What is the minimum size of a solid copper equipotential bonding conductor for a permanently installed pool?
- 10027Perimeter surfaces around a pool must be bonded for what minimum horizontal distance beyond the inside walls?
- 10029A copper ring or grid used for pool perimeter bonding is installed at what depth?