Correct answer to question 10079
- C: They must not have automatic overload protection, only short-circuit and ground-fault protection
Explanation
Fire pump power circuits must not have automatic protection against overloads, except as specifically permitted. Only short-circuit and ground-fault protection are provided so the pump keeps running during a fire.
More questions: Special Equipment, Pools, PV and EV
- 10080During motor starting, the voltage at the fire pump controller line terminals must not drop more than what percentage below the controller rated voltage?
- 10081A fire pump motor has a full-load current of 40 amperes and no accessory loads. What is the minimum ampacity of the supply conductors?
- 10082What is required of a fire pump disconnecting means?
- 10083A transformer arc welder has a rated primary current of 50 amperes and a 50 percent duty cycle. The I1eff value is not marked. Using a duty cycle multiplier of 0.71, what is the minimum supply conductor ampacity?
- 10084The OCPD for an arc welder may be rated at not more than what percentage of the rated primary current (I1max)?
- 10085For a feeder supplying a group of arc welders, what percentage is applied to the two largest welders' current?