Unless the equipment is listed and marked otherwise, terminations for circuits rated 100 amperes or less (or 14 AWG through 1 AWG conductors) are based on which conductor temperature rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1104
- C: 60 degrees C
Explanation
110.14(C)(1)(a) bases termination provisions for these smaller circuits on 60 degrees C conductor ampacity unless the equipment is listed and identified for 75 degrees C. A 90 degree conductor may be used, but its ampacity is limited to the termination rating.