For circuits rated over 100 amperes, or conductors larger than 1 AWG, terminations are generally based on which conductor temperature column?

Exactly one answer is correct.

Show solution

Correct answer to question 1105

  • D: 75 degrees C

Explanation

110.14(C)(1)(b) permits conductors for circuits over 100 A or larger than 1 AWG to be used at their 75 degree C ampacity, unless the equipment is listed for a higher temperature.