A 480Y/277-volt panelboard has exposed live parts on one side of the working space and a grounded concrete wall on the other (Condition 2). What is the minimum depth of working space?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1109
- B: 3.5 feet
Explanation
Table 110.26(A)(1) requires 3.5 feet for Condition 2 at 277 volts to ground (the 151 to 600 V column in NEC 2020, the 151 to 1000 V column in NEC 2023). Condition 1 would be 3 feet and Condition 3 would be 4 feet.