Question 12096 of 1033 · Washington 01 Journey Level Electrician Exam
A 12-unit apartment building qualifies for the NEC 2020/2023 multifamily optional method. The connected load per unit is 30 kVA. What is the calculated load, excluding house loads?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12096
- D: 147.6 kVA
Explanation
12 x 30 kVA = 360 kVA connected. Table 220.84 gives 41 % for 12 to 13 units: 360 x 0.41 = 147.6 kVA. House loads are added using the standard method.
More questions: Load Calculations
- 12097What is the NEC 2020/2023 Table 220.84 demand factor for a building with 4 dwelling units?
- 12098Which is a condition for using the NEC 2020/2023 multifamily optional method of 220.84?
- 12099An existing 200 A service shows a 1-year maximum demand of 110 A. A 40 A load is added. Using NEC 2020/2023 220.87, what is the resulting calculated load?
- 12100Under NEC 2020/2023 220.87, what is the shortest demand recording period permitted where 1-year data is not available?
- 12101Under NEC 2020/2023 220.60, a dwelling has 10 kW of electric heat and a 5,000 VA AC unit that do not run together. What load is used in the standard method?
- 12102An 8-unit building has 900 ft2 units, each with two small-appliance and one laundry circuit. What is the NEC 2020/2023 standard method demand for these loads?