Correct answer to question 5051
- C: At the service equipment or metering equipment, accessible
Explanation
The termination must be accessible for connection and inspection, located at the service equipment or metering equipment enclosure and at the disconnecting means of separate buildings supplied by a feeder. See 250.94.