Question 5053 of 844 · Washington 01 Journey Level Electrician Exam
Metal gas piping that is likely to become energized may be bonded by
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5053
- A: The EGC of the circuit likely to energize it
Explanation
Other metal piping that may become energized must be bonded, and the EGC of the circuit that may energize the piping is permitted to serve as the bonding means. See 250.104(B).
More questions: Grounding and Bonding
- 5054For a separately derived system, where is the system bonding jumper installed under the general rule?
- 5055A transformer supplies 250 kcmil copper secondary conductors. What is the minimum copper GEC for this separately derived system?
- 5056The system bonding jumper of a separately derived system is sized based on
- 5057A detached garage supplied by a feeder must have a grounding electrode system, except where it is supplied by
- 5058At a separate building supplied by a feeder that includes an EGC, the grounded conductor at the building disconnect must be
- 5059Which of these AC systems is required to be grounded?