Question 5052 of 844 · Washington 01 Journey Level Electrician Exam

A service has 3/0 AWG copper ungrounded conductors. What is the minimum copper bonding jumper for the interior metal water piping?

Exactly one answer is correct.

Show solution

Correct answer to question 5052

  • D: 4 AWG

Explanation

The metal water piping bonding jumper is sized from Table 250.102(C)(1) based on the service conductors. For 2/0 or 3/0 copper the jumper must be at least 4 AWG copper. See 250.104(A).

Next to question ›