In NEC 2020 and 2023, aluminum, copper-clad aluminum, or copper conductors may be run in parallel only when they are
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6058
- B: 1/0 AWG and larger
Explanation
Conductors in parallel must generally be 1/0 AWG and larger. The rule is in 310.10(H) in NEC 2020 and 310.10(G) in NEC 2023.